I had to check out the connections to a serial Flash on a new board, and
think it makes a good example of how to debug this.
Looking at the spec sheet for this part, there is a device ID register.
Its a good way to make sure you've got it connected up correctly.
Here's the first program
#include
dim xi(10) as string
dim xo(10) as string
xo(0)=&H90
xo(1)=0
xo(2)=0
xo(3)=0
spiin(31,26,29,30,0,4,xo,2,xi)
print hex(xi(0)),hex(xi(1))
The values that came back were &H91 and &7E and it was repeatable, so
something was hooked up, but still not expected values of &HBF and &H48
A check of the spec sheet showed the data was available as soon as CS is
lowered, so this statement is needed
#define SPIpreSample
Then try to write some data
xo(0)=3
spiin(31,26,29,30,0,4,xo,1,xi) ' read at addr 0
print hex(xi(0))
xo(0)=6
spiout(31,29,30,0,1,xo) ' write enable
xo(0)=2
xo(4)=0xbe
spiout(31,29,30,0,5,xo) ' write 0xbe
wait 10 ' don't know how long it would take, but its less than this
xo(0)=3
print hex(xi(0))
But it still didn't write, back to the spec sheet, and might try reading
the status
xo(0)=5
spiin(31,26,29,30,0,4,xo,1,xi) ' read status
print hex(xi(0))
This was showing &HC which according to the spec means all the memory is
write protected (seems like this is how its shipped from the factory).
So to enable writes this needs to be done
xo(0)=&H50
spiout(31,29,30,0,1,xo) ' status write enable
xo(0)=1
spiout(31,29,30,0,2,xo) ' disable block protect
Not pretty, but a quick test of the interface is done with the following
program it total (notice the xo(1) -(3) values were kept at 0
#include
xo(0)=&H90
xo(1)=0
xo(2)=0
xo(3)=0
xo(0)=5
print hex(xi(0))
xo(0)=&H50
xo(0)=1
xo(0)=3
print hex(xi(0))
xo(0)=6
xo(0)=2
xo(4)=0xbe
xo(0)=5
print hex(xi(0))
wait 10
xo(0)=3
print hex(xi(0))
and the resultant output
Programming Flash 2103...*+
... 3.52K code 0.16K data programmed
Executing...
bf 48
c
ff
0
be
... Finished in 19 ms